Why are my CFM/Ton calculations from Trace with a VAV system and energy wheel so low (150 cfm/ton)? If the ballpark figure is 400 cfm/ton shouldn't I be getting something close to that number?
Nov 4, 2011
Anonymous
I would bet that your system has been reset to 100% outdoor air (this is likely to happen if you are using VAV with std 62.1)
If this is the case, you need to set your max z ration under systems, and the options button. For more information on this, please read: http://energy-models.com/blog/10-1-10/understanding-max-z-ratio
I would bet that your system has been reset to 100% outdoor air (this is likely to happen if you are using VAV with std 62.1)
If this is the case, you need to set your max z ration under systems, and the options button. For more information on this, please read: http://energy-models.com/blog/10-1-10/understanding-max-z-ratio
what is your tons/sf?