Help with modeling Geothermal system

1 post / 0 new

Good Afternoon eQuest users,

I am looking for some help with an equest modeling problem as someone very new to both equest and with just basic understanding of geothermal systems. I was hoping this community could help.

I am trying to model a proposed geothermal system, however the end annual kWh usage in eQuest comes out to be around 25% of the quoted annual kWh usage from the engineer. What am I missing?
This is a building with 4 HVAC zones, each will be served by a waterfurnace system, and there is a ground loop with 2 pumps. The GSHP specs are directly from the geothermal engineer (below and also attached)
I'm also getting some warnings that I'm not sure how to resolve:
1. for each of the 4 systems, " A HEATING-CAPACITY of -29600. is inconsistent with a COOLING-CAPACITY of 38400. in SYSTEM EL1 Sys1 (PVVT) (G.SSE1)
Note: I am using the system sizing that the geothermal engineer forwarded
2. WLHP alarm limits

GSHP Plant Equipment
WS 1 of 2
Water Loop Properties
GSHP Loop: Head: 51
(This is lower, but the lowest equest allows is 51) Design DT: 10 F (a)
Pump Config: Single Loop Pump(s) only Loop Pumps-- Number: 2
Loop Flow: Variable Head/Flow: 23 ft 50gpm
Operation: Demand Setpoint: Fixed Motor Efficiency: Premium
Loop Temp Min: 33F Max: 75F Pump Control: Two Speed

WS 2 of 2
Ground Loop Heat Exchanger Properties
GHX Type: Vertical Well Field Pipe Size: 1 ?? Rating: Specify
Inner: 1.325? Outer: 1.9?
Configuration: Line of 4
U-Tube Leg Separation: 1?
Num of Identical Well Fields: 1 GHX Pipe Head: 30 ft
Depth: 500 ft Spacing: 20 ft Fluid Properties:
Borehole Diameter: 6? Fluid: Methanol
Pipe Material: Polyethylene Antifreeze Concern: 12%

Soil Thermal Properties and History
All settings left to default
[https://energy-models.com/sites/all/files/imagecache/595/forum_topic_field_image_cache/geotherm_properties.PNG]

Kelly  Bucklaew's picture
Offline
Joined: 2026-04-24
Reputation: 0