[Equest-users] Lesson Learned: Single Zone Packaged DX vs. Packaged VAV system types

2 posts / 0 new
Last post

Kristy-

Did you try to use the "WASTE-HEAT-USE" feature of the PSZ system for humidity control?

[cid:image001.jpg at 01CCD544.BCBF0730]

I've had success using this feature to achieve the desired space humidity conditions with 100% OA units.

I can't remember whether its energy performance is appropriate, but I did verify with hourly reports that the zones in question had accurate humidity control.

I remember having a hard time finding this feature - several late nights with the DOE-2 dictionary - but I eventually found the documentation on Vol 2 - Dictionary - pp398-399 and pp416-417.