VAV System hours outside of throttling range- No Load on Heating Coils

2 posts / 0 new
Last post

I have run a Building with a VAV system, pre-heat coils and Zone reheat but
it will not use any load from the condensing boiler. I have thousands of
hours outside of the throttling range. Does any one have any guesses? I
have tried changing the fans to Cycle on any with no luck.

JAMES F. GEERS

James Geers's picture
Offline
Joined: 2011-09-30
Reputation: 0