System 4 - PSZHP Unmet Hours - "undefined" thermostat schedules

2 posts / 0 new
Last post

When you set the zone COOL/HEAT-TEMP-SCH to ?undefined?, there is no thermostat control in the zone and no unmet cooling/heating hours will be reported because the system is not trying to maintain the zone at any particular temperature. The cooling and/or heating thermostat schedules should be defined for at least the control zone of a single zone system.
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP