(no subject)

3 posts / 0 new
Last post

I?m working on a school in Chicago, 5 VAV air handlers, chiller,
boilers, ER piping, a few baseboards. Someone else created the model,
and I?m trying to trouble shoot it now.

I?ve gone through a series of fixes on a few items, and now I?m to a
point that my throttling hours are down within reason. The problem now
is that the BEPS and Equipment reports are showing that I?m providing no
cooling, and very little heating. I can?t find what would be restricting
these items from operating. The strange thing to me is that all the
zones are behaving as if the chiller and boiler were functioning as I
would expect. Any advice on how to diagnose my problem?

I?ve checked schedules, adjusted throttling ranges, compared input
files, etc. Any help would be appreciated.

Pat Furey

Furey, Patrick's picture
Offline
Joined: 2011-09-30
Reputation: 0