KW/Cfm Fan Power Limitation for Baseline & Proposed Model

2 posts / 0 new
Last post

Dear All e-Quest Users

Please If someone can help :

1-KW/Cfm shall be calculated according to Fan Power Limitation method described in ASHRAE 90.1.2007 for the Baseline Method , but what about Proposed Model please ???

Should I used the same method for Proposed model to calculate the KW/Cfm but sure using the Cfm of Proposed Model ????

Thanks by Advance for all of u ??.

My Regards,
Riad el Abed
Chief MEP , LEED GA,PQP

Riad el Abed's picture
Offline
Joined: 2011-12-07
Reputation: 0