Dear all
As per ASHRAE 90.1 HVAC System 7 is Packged rooftop VAV with Reheat and
cooling type is Chilled water.
How can we model above HVAC System in eQUEST.
If I choose Cooling source as Chilled water coils than it donot show
any Packaged system in System Type drop-down.
--
With Thanks and Regards,
Praveen K. Jain
use VAV type system. Typically packaged is for DX units. i am doing the
same thing in a model right now as well.
Praveen, System Type 7 is actually VAV w/reheat, chillled water
coils....etc.
The "packaged" that is printed in front of it is a "typo" in the
Standard. You should use the non-packaged option for your baseline model.
Pasha
Is there a chart somewhere that explains which system is what in the baseline? i.e. ASHRAE 90.1 System 1 = eQuest System "Var Air Vol", etc etc etc?
William Mak, LEED Green Associate
William:
ASHRAE 90.1 Table G3.1.1A and 1B.
Paul Diglio