Is there such an animal in eQuest or is there a workaround?
Thanks in advance.
John R. Aulbach, PE

John Aulbach's picture
Offline
Joined: 2011-09-30
Reputation: 1

Yes and yes.

There is indeed a heat pump type DHW heater in eQUEST. Note that this is an air source heater with the condenser outside. As such, the COP diminishes quite a bit from the rated value in colder climates.

If instead you have a water source heat pump with a relatively stable condenser temperature and COP, I tend to model with an electric DHW heater with an EIR of 1/COP.

Brian

Footprint

Brian Fountain's picture
Offline
Joined: 2019-05-02
Reputation: 0

To foot stomp the condenser note; the default performance curves seem to be extremely conservative compared to equipment available today.