I am using the refrigeration version of equest 3.61 and have several zones within the building which have exterior walls and roof. The equest output notes loads in cooling for them but not in heating while other zones properly indicate loads for both cooling and heating, has anyone else run across this and can suggest something for me to check. The output is listed below.
REPORT- LS-B Space Peak Load Components EL1 NNE Perim Spc (G.NNE16) WEATHER FILE- Baltimore MD TMY2
---------------------------------------------------------------------------------------------------------------------------------
SPACE EL1 NNE Perim Spc (G.NNE16)
SPACE TEMPERATURE USED FOR THE LOADS CALCULATION IS 70 F / 21 C
MULTIPLIER 1.0 FLOOR MULTIPLIER 1.0
FLOOR AREA 28544 SQFT 2652 M2
VOLUME 513785 CUFT 14550 M3
COOLING LOAD HEATING LOAD
========================== ==========================
TIME AUG 3 7PM
DRY-BULB TEMP 93 F 34 C
WET-BULB TEMP 76 F 24 C
TOT HORIZONTAL SOLAR RAD 80 BTU/H.SQFT 252 W/M2
WINDSPEED AT SPACE 5.3 KTS 2.7 M/S
CLOUD AMOUNT 0(CLEAR)-10 0
SENSIBLE LATENT SENSIBLE
(KBTU/H) ( KW ) (KBTU/H) ( KW ) (KBTU/H) ( KW )
-------- ------ -------- ------ -------- --------
WALL CONDUCTION 4.394 1.287 0.000 0.000 0.000 0.000
ROOF CONDUCTION 28.204 8.264 0.000 0.000 0.000 0.000
WINDOW GLASS+FRM COND 0.000 0.000 0.000 0.000 0.000 0.000
WINDOW GLASS SOLAR 0.000 0.000 0.000 0.000 0.000 0.000
DOOR CONDUCTION 0.000 0.000 0.000 0.000 0.000 0.000
INTERNAL SURFACE COND 0.000 0.000 0.000 0.000 0.000 0.000
UNDERGROUND SURF COND -0.666 -0.195 0.000 0.000 0.000 0.000
OCCUPANTS TO SPACE 18.451 5.406 15.444 4.525 0.000 0.000
LIGHT TO SPACE 144.060 42.209 0.000 0.000 0.000 0.000
EQUIPMENT TO SPACE 0.000 0.000 0.000 0.000 0.000 0.000
PROCESS TO SPACE 0.000 0.000 0.000 0.000 0.000 0.000
INFILTRATION 1.692 0.496 2.090 0.612 0.000 0.000
-------- ------- ------- ------ -------- --------
TOTAL 196.134 57.467 17.534 5.137 0.000 0.000
TOTAL / AREA 0.007 0.022 0.001 0.002 0.000 0.000
TOTAL LOAD 213.669 KBTU/H 62.605 KW 0.000 KBTU/H 0.000 KW
TOTAL LOAD / AREA 7.49 BTU/H.SQFT 23.609 W/M2 0.000 BTU/H.SQFT 0.000 W/M2