I am getting (2standard file writing errors encountered) error while running my
simulation can any one help me out to resolve this issue. Please find the
attachments.
Your 3-D building view is all distorted. I returned to Wizard Mode and saw that
all three floors are unconditioned on screen 13. I assigned HVAC system 1 to
all three floors. HVAC system 1 was defined with no heating or cooling, so I
defined it as a heat pump. Then the simulation works ok.
Some of your custom zones in the Wizard screen 2 are not square. Look at the
vertices X-Y coordinates when you select a zone and you will see some of the
numbers are off. You can type in the X-Y coordinates directly in the left hand
column instead of trying to straighten them out with the mouse.
Ramesh:
Your 3-D building view is all distorted. I returned to Wizard Mode and saw that
all three floors are unconditioned on screen 13. I assigned HVAC system 1 to
all three floors. HVAC system 1 was defined with no heating or cooling, so I
defined it as a heat pump. Then the simulation works ok.
Some of your custom zones in the Wizard screen 2 are not square. Look at the
vertices X-Y coordinates when you select a zone and you will see some of the
numbers are off. You can type in the X-Y coordinates directly in the left hand
column instead of trying to straighten them out with the mouse.
Paul Diglio