Hi,
I had a query whether ASHRAE 90.1 mentions what value has to
be taken for wall and roof absorptance as it mentions for U value . As
absorptance value has great impact on heat gains and further on energy
consumption.

Can we have a better wall absorptance in proposed case from base case
so to improve energy performance

Any response will be highly appreciable.

Thanks
Sambhav Tiwari.

sambhav tiwari's picture
Offline
Joined: 2011-09-30
Reputation: 0

Table G3.1 5c (for Proposed) and 5d (for Baseline) mentions how to model the reflectance (1-absorptance) of both the baseline and proposed roof. The baseline must be modeled with a reflectivity of 0.3. The proposed must be either 0.3, or 0.45 if the proposed roof has a reflectance of 0.7 or greater.

I have not seen anything in 90.1 about modeling the reflectance of walls.

Frank

Frank Hartley's picture
Offline
Joined: 2011-09-30
Reputation: 0

Hello Sambhav,

In regard to exterior surface solar reflectance, ASHRAE 90.1 focuses only on
roofs and not walls. In the 90.1-2007 version, Table 5.5.3.1 has U-Factor
requirements for high albedo roofs (formerly referred to as "cool roofs".)
This single table is a replacement for the roof U-Factor requirements found
in Tables 5.5-1 through 5.5-3 (i.e., climate zones 1 through 3.) The
definition of "high albedo" is found earlier in Section 5.5.3.1.1 as roofs
with a minimum Solar Reflective Index (SRI) of 0.82. Typically, this is a
roof of high emissivity as well as high reflectance. The 90.1 User's Manual
shows values that achieve an SRI of 0.82 in Table 5-D, ranging from an
(e=0.75, refl=0.7) to (e=0.1, refl=0.81) combinations.