Hi All,

I have found this guideline for Baseline Chiller Plant Modeling
for capacity <300 TR. I just wanted to know is it acceptable by USGBC? What will be the methodology for Plant >300 TR?

Please find the parent link for this attachment.

http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2010-November/006884.html

Thanks

--

*Javed Iqbal, LEED AP, CEA*

javed's picture
Offline
Joined: 2011-04-11
Reputation: 0

Javed,

The guideline was created to create the chiller plant defined by ASHRAE
90.1 Appendix G which is used for LEED modeling and accepted by USGBC.
This information is located in Appendix G Section G3.1.3.7 through
G3.1.3.10, which if you don't have a copy of Appendix G, it is a
must-have. It basically states for plants greater than 300 tons, you
will have variable speed pumps on the secondary loop instead of the
pumps riding the pump curve. You will also have 2 chillers for plants
helps!

Thanks,

Matthew Larson, LEED AP BD+C