Dear All,
Would somebody kindly point me to where I can find the performance
curves for VRF systems released by Mitsubshi. I have searched previous
postings and looks like they were previously shared as email
attachments, but I cannot download those attachments.
Thanking you in advance,
?mer Moltay, LEED AP BD+C, ASHRAE BEMP, ASHRAE CPMP
Mimta EcoYapi, LEED Proven Provider
Hekimsuyu Cad. 559. Sk.
No:39 34255 Kucukkoy Istanbul Turkey
Tel: 90-212-617-2296
Fax: 90-212-617-2297
Mobile: 90-533-957-1394
www.eco-yapi.com
www.buildingenergymodels.com
Hi ?mer,
If you are using the newest eQUEST running in DOE-2.3 (version 3-65 Build 7175), there are no custom manufacturers VRF curves available to the public, to my knowledge. If you are reading this and you work for Mitsubishi, Trane, Daikin, LG, York or Hitachi (or if you manufacture VRF equipment but I didn?t list your company) ? this is a missed business opportunity and you should contact me!
I would recommend you use Build 7175 in DOE-2.3 mode if you have VRF systems to model, as VRF capability was specifically added and none of the DOE-2.2 workarounds are required (though there is still no built-in capability for water-source VRF).
If you have a DOE-2.2 model and would still like access to the workaround by Mitsubishi, let me know and I?ll email the files that I have archived.
Best regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005 www.pathfinder-ea.com
bbishop at pathfinder-ea.com
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image004.png at 01D68AB8.9020C2D0] Ask me why Carbon Fee & Dividend may be right for you.
Hi Bill,
We are using eQuest v3.64. So I would appreciate if you can send me
those files.
Best,
?mer Moltay, LEED AP BD+C, ASHRAE BEMP, ASHRAE CPMP
Mimta EcoYapi, LEED Proven Provider
Hekimsuyu Cad. 559. Sk.
No:39 34255 Kucukkoy Istanbul Turkey
Tel: 90-212-617-2296
Fax: 90-212-617-2297
Mobile: 90-533-957-1394
www.eco-yapi.com
www.buildingenergymodels.com
Hi Bill,
I have worked with the eQuest 3.65 build 7175 and DOE 2.3 for VRF modeling.
I have an issue with VRF control:
The model was for cold climate conditions and VRF was supposed to be cut out for another heat source around -15 C. To compensate VRF capacity before -15 C I had to have another heat source supplying too. This kind f behavior can be managed in DOE 2.2 in the heat pump settings. As for DOE 2.3 I didn?t find this kind of options into the VRF tabs.
Did you encounter this kind of problem? If yes, how did you manage it?
Thanking you in advance,
[cid:image001.jpg at 01D68CB8.DAED1550]
Christophe Genev?s_ing.
D?veloppement durable et Efficacit? ?nerg?tique
cgeneves at bpa.ca | t: 5143833747x2819
De : Omer Moltay
Envoy? : 16 septembre 2020 11:23
? : Bishop, Bill
Cc : equest-users at lists.onebuilding.org
Objet : Re: [Equest-users] VRF Performance Curves for Mitsubishi
Hi Bill,
We are using eQuest v3.64. So I would appreciate if you can send me those files.