Agreed.
Read any other way, the baseline allowances would arbitrarily ?penalize?
the performance rating of any building NOT lighting up all their
driveways/facades like a Vegas strip? not in keeping with the general
thrust of an energy standard.
~Nick
*NICK CATON, P.E.*
*Owner*
*Caton Energy Consulting*
1150 N. 192nd St., #4-202
Shoreline, WA 98133
office: 785.410.3317
www.catonenergy.com
*From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] *On Behalf
Of *Cam Fitzgerald
*Sent:* Thursday, January 22, 2015 2:56 AM
*To:* 'John Aulbach'; bldg-sim at onebuilding.org
*Subject:* Re: [Bldg-sim] Simple LEED type question-actually for a utility
program
John,
The allowance is determined using only the applications that are actually
illuminated in the design. If the design does not include any non-tradable
lighting applications, then none is modeled in either case. For any
application in the design, it is not the area or length that could
potentially be illuminated, but the actual illuminated area or length that
is used to determine the baseline allowance.
Hope that helps,
Cam Fitzgerald
Energy Opportunities/a 7group company
*From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org
*Sent:* Wednesday, January 21, 2015 11:01 PM
*To:* bldg-sim at onebuilding.org
*Subject:* [Bldg-sim] Simple LEED type question-actually for a utility
program
If there is NO outdoor lighting on the building (except entrances), such as
building facade lighting, does the ASHRAE 90.1 version of facade lighting
have to be input to BOTH Base and proposed buildings? Or can it be left out
all together?
Thanks in advance.
John R. Aulbach, PE