Hi All,
I am working on a LEED Energy model for a 8 floor Office Building. The
Baseline System type I have is Type 8 -VAV with PFP boxes / Chilled
Water-cooling, Electric Heating.
Now, the proposed building has Water cooling unitary units with a single
Outside Air unit. The outside air is supplied to mechanical room on each
floor through a ducted shaft with each floor having its own VAV box to
control the OA. Also, there is one single cooling tower that is used as a
Heat rejection equipment. I am doing this model in TRACE, so all the trace
experts are welcomed to answer this as well.
1. Since i have a Dedicated Outside Air Unit, I should model the outside
air fan for the baseline as well and allow it be sized based on PRM method
? Now, TRACE does not allow me to create a overall Air side system type
Outside air unit and thus i have to basically provide a Optional
Ventilation fan on each unit (i guess this is limitation but i cant think
of other way) for the Baseline. Also, TRACE only allows 90.1 Fan power
adjustment to Primary fan (Supply fan) so i will not be able to take any
credit for fan power adjustment on Outside air fan for using better filters.
Similarly, for proposed building i have to model the Optional Ventilation
Fan but this would be based on my actual selection. The selection i have is
for Dedicated Outside Air fan. Is it safe to assume the proposed outside
air fan power in "KW/CFM" from the actual selection for the energy
consumption?
2. Similar to point 1, TRACE does not allow to create a single plant as a
heat rejection equipment for all the Indoor units. Thus, based on my
selection for cooling tower , condenser water pump, is it safe to simulate
the proposed building with cooling tower and pump for each water cooled
unitary system with the same KW/TON and Watts/GPM respectively?
Finally, if i do the above mentioned things in simulation, does anyone else
have any experience with this kind of situation for the LEED model. I can
explain everything in Narrative (that these are limitations of Modeling
software), but i am afraid what the LEED reviewer may or may not approve
and if he/she does not approve, would he/she suggest a way of doing it the
right way or not.
Any thoughts, suggestions are greatly appreciated.
--
Thanks
Sincerely,
Amit Bhansali