LEED Online Form - Number of Heating / Cooling Hours Not Met

2 posts / 0 new
Last post

Dear All,

LEED online form requests unmet hours for heating and cooling to be
entered separately.

1. Is it possible to extract this information from any of eQuest reports?
2. Isn't this counterintuitive? There will be overlapping hours for both
heating and cooling. The form adds these hours (double counting any hour
where there is both a heating load unmet and cooling load unmet) and
requires the addition to be smaller than 300. As far as I know, the
combined number of hours need to be smaller than 300.

Thanks for any replies,

Omer Moltay, LEED AP

Omer Moltay's picture
Offline
Joined: 2011-09-30
Reputation: 0