HI,
I am modeling a very large building, approx. 259,000 sqft, with several subsections of buildings. The subsections are as follows:
bus service area 84,800 sqft with office area 5720 sqft
bus parking area 143,300 sqft
2 story admin building 25,100 sqft
The service, and parking area are going to be heated to 55 only, while the office areas will be heated and cooled. My question is for the baseline model do I need to have one AHU serving the whole first floor, essentially 246,000 sqft, or could I use exception a. to G3.1.1? Would heating setpoint be classified as "nonpredominant conditions"? I would like to use separate system 7 AHUs (5 units for the above areas), the reason being that I can avoid modeling heat recovery in the baseline model with these systems separated.
the exception reads:
Use additional system type(s) for nonpredominant conditions (i.e., residential/nonresidential or heating source) if those conditions apply to more than 20,000 ft2 of conditioned floor area.
Any insight would be appreciated.
Thanks,
Matthew J. Baron, PE
[wendel EM]
Wendel, 140 John James Audubon Pkwy, Suite 201, Buffalo, NY 14228
p 716.688.0766 f 716.625.6825 e mbaron at wendelcompanies. com w wendelcompanies. com
ARCHITECTURE ENGINEERING PLANNING ENERGY SERVICES CONSTRUCTION MANAGEMENT
CONFIDENTIALITY NOTICE: This email transmission is confidential and is intended only for the person(s) named above. Its contents may also be protected by privilege, and all rights to privilege are expressly claimed and not waived. If you have received this email in error, please call us immediately and destroy the entire email. If this email is not intended for you, any reading, distribution, copying or disclosure of this email is strictly prohibited.
Please consider the environment before printing this email.