I am looking for pointers for modeling ice arenas. This project has a typical ice plant. Condenser heat recovery is used for the warm water loop below the insulation, adjacent the soil to prevent freezing. The condenser heat recovery is also used for DHW preheat for the Zamboni hot water and for the snow-melt pit. There is a desiccant dehumidifier to maintain RH in the arena.
Any ideas, papers, etc. appreciated.
[cid:image001.jpg at 01D2A6E9.840756F0]
Christopher R. Jones, P.Eng.
Technical Specialist
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
T +1 416-644-0252
www.wspgroup.ca
Please consider the environment before printing...
Chris,
eQUEST has some capability to model ice rinks. In the ?Air-Side HVAC? module select the appropriate zone, then click on ?Spreadsheet? at the top. For the Display Mode select ?Ice Skating Rinks? at the very bottom of the list. There is a similar spreadsheet in the ?Water-Side HVAC? module. These inputs are available only in the spreadsheet view, not in the classic window view.
I started using these ice rink inputs years ago for an ice rink and ran into a roadblock. I think it had something to do with eQUEST not accepting the brine temperature or the deltaT. Anyway, I ended up doing spreadsheet calcs for the refrigeration system (compressors, pumps, floor heat, low emissivity ceiling, etc.) and another program for the rest of the building. The effect of the cooling from the ice on the HVAC system can be modeled as a process load with a negative heat gain.
Keith Swartz, PE | Senior Energy Engineer
Seventhwave
608.210.7123 seventhwave.org
Thank you Keith.
[cid:image001.jpg at 01D2A6E9.840756F0]
Christopher R. Jones, P.Eng.
Technical Specialist
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
T +1 416-644-0252
www.wspgroup.ca
Please consider the environment before printing...