HP Model

2 posts / 0 new
Last post

Hi All,
I'm modeling a 6 stories building with a HP HVAC system, This system includes a condenser boiler and a cooling tower, I have some warning messages, I would greatly appreciate if somebody help me to find the variable that I have to modify to get rid of these messages.
One extra questions what the best way to reduce the throttling range?

Thanks for your help.

**WARNING**********************************************************************

Loop: WLHP Water Loop heating capacity is smaller

than the secondary demand. Primary= -2400000.

Secondary= -3290026.

**WARNING**********************************************************************

Loop: WLHP Water Loop cooling capacity is smaller

than the secondary demand. Primary= 2580000.

Secondary= 4062237.

**CAUTION**********************************************************************

In curve: FluidCooler-FluidCap-fRng&WB the dependent value

is exceeding the limits.

Value/Min/Max/First time: 4.981 0.000 3.000 5/ 5/22

**CAUTION**********************************************************************

In curve: FluidCooler-FluidCap-fApp&WB the dependent value

is exceeding the limits.

Value/Min/Max/First time: 3.005 0.000 3.000 5/25/23

William G. Lopez, CEM

William Lopez's picture
Offline
Joined: 2011-09-30
Reputation: 0

Thank you Haddad,
I got rid of the heating and cooling capacities warnings, but the caution about the curves still persist.

William Lopez's picture
Offline
Joined: 2011-09-30
Reputation: 0