All;
Have a model where a MultiStack Air-Source HP Chiller/Boiler is being considered. This unit is air-source and can operate in cooling only, cooling & heating, or heating only. Hot Water loop will have Electric Boiler as back-up/supplemental. Climate 4A. Air Side is a Multizone VAV with HW / CHW.
Only resource I found online is quite dated, from Dana Troy in September 2011. However, that write-up was using a ground coupled system for loop imbalance, my potential design will not.
Within eQuest I found the Type: Heat Pump Chiller, but it must be tied to a single Chilled Water or a 2Pipe Loop. The first work around I tested was to create two loops (Chilled Water and 2Pipe) with double the normal number of chillers and use equipment controls for sequencing. The 2Pipe loop had a High Snap temperature to always keep it in heating mode & act as the Hot Water Loop. The Air-Side allowed Chilled Water loop assignment for cooling, and allowed the 2Pipe Assignment for Heating and Zone Heating. Though, this run resulted in 3000+ unmet hours and the Chilled Water Loop to attempt to operate at 70F. If the Heating source to changed to electric, the unmet hours decrease and the loops control as expected. If I change the Heating Source to a separate dummy/test Hot Water loop, this too allows proper operation. It would appear that when attempting to assign a 2Pipe loop to both Heating and Zone Heating causes the Chilled Water Loop to misbehave(?!). Anyone else experienced this or have other solutions?
In an effort to work around this issue, I swapped the Heat Pump to a Loop-to-Loop Heat Pump Option. This allowed the creation of a Hot Water & Chilled Water loop - but also requires a Lake/Well Loop. Luckily, a Ground Loop Heat exchanger can take a schedule of temperatures. Thus, I extracted the Outside Air temperature to an 8760 schedule and assigned this to the Ground Loop Heat Exchanger. This way the loop is ~to the OA temp, but having doubts that this is legitimate as I am seeing a significant delta in the hourly reports between the Loop Temperatures and the OA Temp for some hours.
Open to ideas. Thanks in advance.
Thanks,
DARIC ADAIR PE, CEM, BEMP
Mechanical Engineer, Energy Analyst
HENDERSON ENGINEERS
daric.adair at hendersonengineers.com
LICENSED IN KS
HENDERSON PROUD SINCE 1970
________________________________
This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hendersonengineers.com.