Hi all,
I´am trying to model a room that as the amount of ventilation following room temperature, my difficulty is that i can only do schedules that follow other parameters.
I´m trying to adjust the amount of direct OA (no coil) during the day, to maintain the room temp constant, so the room can benefit with the outside temperatures.
Can somewone help ?
Sorry if it sounds confusing...
Kind Regards
This goes a bit beyond the intent of TRACE 700.
HOWEVER, there is a way you can do this.
On the naturally ventilated room, I would use "infiltration" and set an infiltration schedule with a reset and lockout temperature. IN the room, set the infiltration to the maximum amount of natural ventilation (this part is easy). In the schedule,I'd start with the ventilation set to 0, and then raise it in increments based on the room tempertature
see the attached image
Thanks,
I´m going to try this...