I wanted to confirm the following:
If I create a baseline model with Custom Lyr-by-Lyr construction, I cannot create an EEM with less insulation than the baseline? The detail wizard only gives me the option of additional Insulation.
Thanks.
[cid:image001.png at 01CE02E8.2DB751A0]
MICHAEL RAIVA, P.Eng., LEED(r) AP
You will have to use the whole building measure option.
Brian Fountain
bfountain at greensim.com
I can't recall what SV-A reports for self-sized air flows - the
"single" space air flow or the multiplied space air flow. In other
words does DOE2 self size the zone air flow based on a single space?
>> Christopher Jones, P.Eng.
Chris,
I believe the zone-level air flows reported in the SV-A are for a single zone. The end of
each line shows the ZONE MULT that gives the zone multiplier that is used by DOE-2 in
calculating the total air flow rate that needs to be supplied by the central fans. I'm
not sure, but I don't think the coincidence, i.e., diversity, of these zone air flows are
considered when they are added up.
Joe