Modeling Ashrae - System 8 in equest - Fan in the parallel box

1 post / 0 new

Hi Konstantina,

As per me you are correct in finding the Fan power for system type-8 which
comes as 0.35 W/ cfm. as per G 3.1.3.14.

The thing that you are required to have is the same kind of input in the
Airside system fan power parameters.
As an example following snapshot has been provided.

[image: image.png]

Hope this might help.

*Thanks and Regards*,
Sharad.Kumar
Freelancer
India

*From:* Equest-users *On
Behalf Of *Konstantina Kalliakoudi via Equest-users
*Sent:* Tuesday, July 30, 2019 8:44 AM
*To:* equest-users at lists.onebuilding.org
*Subject:* [Equest-users] Modeling Ashrae - System 8 in equest - Fan in the
parallel box

CAUTION: EXTERNAL SENDER

Dear equest users,

According G3.1.3.14 for system 8 the fan parallel box shall be modeled with
0.35 W/cfm fan power.

I was wondering where this paramater can be insered in equest.

In the following screenshot I have input the power of the supply fan.

[image: image.png]

Thank you very much.

Best regards

Konstantina Kalliakoudi

Mechanical Engineer ?.Sc.

www.khmoe.gr

Sharad Kumar2's picture
Offline
Joined: 2015-05-21
Reputation: 0