Hi Konstantina,
As per me you are correct in finding the Fan power for system type-8 which
comes as 0.35 W/ cfm. as per G 3.1.3.14.
The thing that you are required to have is the same kind of input in the
Airside system fan power parameters.
As an example following snapshot has been provided.
[image: image.png]
Hope this might help.
*Thanks and Regards*,
Sharad.Kumar
Freelancer
India
*From:* Equest-users
Behalf Of *Konstantina Kalliakoudi via Equest-users
*Sent:* Tuesday, July 30, 2019 8:44 AM
*To:* equest-users at lists.onebuilding.org
*Subject:* [Equest-users] Modeling Ashrae - System 8 in equest - Fan in the
parallel box
CAUTION: EXTERNAL SENDER
Dear equest users,
According G3.1.3.14 for system 8 the fan parallel box shall be modeled with
0.35 W/cfm fan power.
I was wondering where this paramater can be insered in equest.
In the following screenshot I have input the power of the supply fan.
[image: image.png]
Thank you very much.
Best regards
Konstantina Kalliakoudi
Mechanical Engineer ?.Sc.
www.khmoe.gr