Would anyone like to share an input file (or paste the text into an email) with all the fan curves described in the EDR resource below? (Advanced Variable Air Volume VAV System Design Guide
I offer the following curve-fit for Appendix G., Table G3.1.3.15 for any of you that don't already have it for your LEED Baseline models. (Just copy and paste into the "Performance Curves" section of the input file.):
"App G VAV Fan FPLR" = CURVE-FIT
TYPE = CUBIC
INPUT-TYPE = COEFFICIENTS
COEFFICIENTS = ( 0.0013, 0.147, 0.9506, -0.0998 )
..
Thanks,
Bill