Differential pressure reset on CHW Loop

2 posts / 0 new
Last post

I am trying to capture pumping energy savings attributed to applying
differential pressure reset on CHW loop. I am changing the head set point
control from fixed to valve reset in parametric runs but I don't see any
energy savings. I even tried changing the sensor location from "entering
loop" to "at coils" but no luck. Can anyone help in figuring out why I am
not getting savings. Thanks!

kshekhlia's picture
Offline
Joined: 2013-08-19
Reputation: 0

Hi,

Do you have a variable speed pump? More importantly do you have two way valves?

Best,
Julien