Chiller hourly profile

4 posts / 0 new
Last post

Hello,

Is there way to generate chiller hourly profile in eQuest. I am able to get
cooling load profile for CHW circulation loop. however, i am specifically
looking for individual chiller serving the loads. Any insight would be
highly appreciated.

Thanks in advance.

--

Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst

javed's picture
Offline
Joined: 2011-04-11
Reputation: 0

Thank you, Jones and John for your guidance. It helped me.

Merry Christmas.

javed's picture
Offline
Joined: 2011-04-11
Reputation: 0

Create a new hourly report. Enter a unique name. For Variable Type, select the chiller you are concerned with.

Christopher Jones, P.Eng.
Tel: 416.644.4226 * Toll Free: 1.888.425.7255 x 527

Chris Jones
crollinjones's picture
Offline
Joined: 2013-12-12
Reputation: 0

One curve ball you need to consider. If you only just put in multiple chillers, all chillers will rise and fall the same, as they will share the load. You need to use Equipment-Quad to fire the chillers in the sequnces you want.
But as far as i know, what ever chillers are running at a particular time share the load.
Make sure this is how your intended operation goes.
John R. Aulbach, PE

#yiv7360993904 #yiv7360993904 -- _filtered #yiv7360993904 {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;} _filtered #yiv7360993904 {font-family:Tahoma;panose-1:2 11 6 4 3 5 4 4 2 4;} _filtered #yiv7360993904 {panose-1:2 11 5 3 2 1 2 2 2 4;} _filtered #yiv7360993904 {panose-1:2 11 6 3 2 2 2 2 2 4;}#yiv7360993904 #yiv7360993904 p.yiv7360993904MsoNormal, #yiv7360993904 li.yiv7360993904MsoNormal, #yiv7360993904 div.yiv7360993904MsoNormal {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;}#yiv7360993904 a:link, #yiv7360993904 span.yiv7360993904MsoHyperlink {color:blue;text-decoration:underline;}#yiv7360993904 a:visited, #yiv7360993904 span.yiv7360993904MsoHyperlinkFollowed {color:purple;text-decoration:underline;}#yiv7360993904 span.yiv7360993904EmailStyle17 {color:#1F497D;}#yiv7360993904 .yiv7360993904MsoChpDefault {} _filtered #yiv7360993904 {margin:1.0in 1.0in 1.0in 1.0in;}#yiv7360993904 div.yiv7360993904WordSection1 {}#yiv7360993904 Create a new hourly report. Enter a unique name. For Variable Type, select the chiller you are concerned with. ? ? Christopher Jones,P.Eng.