Hi all,

I'm looking for guidance on which number to use for my baseline OA when compared to the proposed system.

The proposed HVAC system is DOAS - FCUs. OA requirements according to ASHRAE 62.1 are 10,216 cfm. However, to satisfy exhaust requirements, the total system ventilation, i.e. OA as it's a DOAS, is 13,160 cfm.

Does the baseline OA need to equal 10,216 or 13,160 cfm?

Thanks

D?nal

Dónal OConnor's picture
Offline
Joined: 2011-10-02
Reputation: 0

In my opinion, the baseline case OA should be equal to the proposed OA. OA required by 62.1 is only a basis for reference.
Xing

Hi all,

I'm looking for guidance on which number to use for my baseline OA when compared to the proposed system.

The proposed HVAC system is DOAS - FCUs. OA requirements according to ASHRAE 62.1 are 10,216 cfm. However, to satisfy exhaust requirements, the total system ventilation, i.e. OA as it's a DOAS, is 13,160 cfm.

Does the baseline OA need to equal 10,216 or 13,160 cfm?

Thanks

D?nal

rockymtn's picture
Offline
Joined: 2011-10-02
Reputation: 0

Hi Donal,

As OA in the proposed model must equal the OA in the baseline model so you
have to use 13,160 CFM (better energy saving chance on the proposed than
10,216 CFM).

There are more details on Example 6-III "Calculation of Fan Power Energy,
Floor-by-Floor System" at ASHRAE 90.1-2007 User's Manual

Best Regards,

Wahid H. Mohamed, LEED AP BD+C

Wahid Hamed's picture
Offline
Joined: 2012-03-05
Reputation: 0

Hi all,

Thank you for your input.

Cheers

D?nal

Date: Sat, 11 May 2013 12:34:55 +0300
Subject: [Bldg-sim] Baseline VAV OA vs Proposed DOAS OA
From: wahid.hamed at gmail.com
To: oconnor_dj at hotmail.com
CC: bldg-sim at lists.onebuilding.org

Hi Donal, As OA in the proposed model must equal the OA in the baseline model so you have to use 13,160 CFM (better energy saving chance on the proposed than 10,216 CFM).
There are more details on Example 6-III "Calculation of Fan Power Energy, Floor-by-Floor System" at ASHRAE 90.1-2007 User's Manual

Best Regards,

Wahid H. Mohamed, LEED AP BD+C

Dónal OConnor's picture
Offline
Joined: 2011-10-02
Reputation: 0