VSD fans does not show saving in eQUEST Software

2 posts / 0 new
Last post

Hello Guys and happy Easter for all,
I am modeling an aged care facility with Water Source Heat Pump (WSHP) units with constant speed supply fans in eQUEST software. I want to get the savings in energy if we install variable speed drive (VSD) on the supply fans. I setup a parametric run for this EEM, but the results after I run the simulation don't show any saving.?
Did anybody encounter something like that? I appreciate any help that let me solve this problem.?The eQUEST files are attached for this project.
Thank you all and regards
Ahmad

Ahmad Fraij's picture
Offline
Joined: 2020-10-13
Reputation: 0

In order to share your parametric run, you will also need to share the .prd file.

Is the minimum flow ratio set to less than 1 in the parametric run?? It can be set at either the system or zone level.? I would suggest system level.? If both, zone level input supercedes.?

If you look at the ss-r report, is the airflow less than 100 percent for most zones?

The ss-L report shows details on fan power and in general eQUEST will show fan power savings with the ECM you describe.