[TRNSYS-users] Type 673 heating problem

2 posts / 0 new
Last post

Dear all,

I cant make type673 heating mode to work. Cooling mode works just fine but
when I change the cooling control signal to 0 and heating control signal to
1 it doesnt work anymore. When the heating mode is used nothing happens.
Does anyone know why?

Best regards,
Santeri Siren

Santeri Siren's picture
Offline
Joined: 2016-04-05
Reputation: 0

Dear Santeri Siren,

I just tested it, and it seems to function
properly. Please make sure that you view the "More" button about the
sensible heating load. You will notice that heating loads are defined as
negative.

Best regards,

Matt Duffy

On 2012-06-11 11:56, Santeri
Siren wrote:

work. Cooling mode works just fine but when I change the cooling control
signal to 0 and heating control signal to 1 it doesnt work anymore. When
the heating mode is used nothing happens. Does anyone know why?