Transfer / makeup air

2 posts / 0 new
Last post

Hi,
We're modeling a system with an exhaust hood, where the makeup air comes from other systems within the building. Is there a way of specifying the source of the makeup air, or do we need to fake it?

Thanks in advance for your help,

James P. Crockett, P.E. 

Crockett, Jim's picture
Offline
Joined: 2011-09-30
Reputation: 0

DOE-2 forces a mass balance at the zone level and does not transfer air
between zones.

To my mind, you would be best to split your exhaust into the zones that it
is being transferred/made-up from.

Further to this, note that zonal exhaust is not available for heat
recovery so if you are recovering heat from the exhaust air stream, you
will need to specify it as central exhaust rather than zonal exhaust. Not
an issue if there is no heat recovery.

Good luck

Brian