System multiplier

2 posts / 0 new
Last post

I'm modeling a building with multiple zones per floor. Each floor is
supplied by two identical air handlers supplying 26,000 cfm each. I
would like to model it as a single system. Should I:

1. Model a single AHU with 26,000 cfm and assign it a multiplier
of 2 (system sizing ratio)

2. Model a single AHU with 52,000 cfm without the sizing ratio
(sizing ratio 1).

3. Model both air handlers (would prefer not to).

Vikram Sami, LEED AP

Vikram Sami's picture
Offline
Joined: 2011-09-30
Reputation: 0

Vikram,

When you use a sizing ratio of 2, you're oversizing the system by 100%
while the loads stay at 1/2 of what they should be. This is not what you
want.

Depending on the system type, using a single unit with 52,000 cfm can
affect the results because of the different load diversity.

Kamel Haddad