I've got a project on my hand in which the electrical demand reported in the PS-E report doesn't match the billing demand in the ES-E report.
I've found that this was due to the "demand interval" of 15 mins on the utility meter. Fixing the demand interval to 60 mins solved the matching demand problem between the PS-E and ES-E report.

I'm just curious as how does eQUEST calculate subhour demand and determined that some electric heating power in my building didn't last more than 15min.
I need a captain here. Anyone can enlighten me?

Thanks,

[Bouthillette Parizeau]

Patrick Lapierre_ing.
plapierre at bpa.ca | www.bpa.ca | t: 5143833747x2807

Les informations contenues dans le courriel que vous venez de recevoir, y compris les pi?ces jointes, sont destin?es ? l'usage exclusif de la (ou des) personne(s) identifi?e(s) comme destinataires et sont confidentielles. Si vous n'en ?tes pas le destinataire, soyez avis? que tout usage en est interdit. Si vous avez re?u ce courriel par erreur, veuillez le retourner ? l'exp?diteur et le supprimer compl?tement de votre syst?me informatique.