Simulating Heat Pump Chiller in eQuest Software

3 posts / 0 new
Last post

Hello Everyone,
I am trying to simulate heat pump chiller in eQuest software but I could not. I know that I can select heat pump chiller in the detailed mode but how to connect it to the hot water loop and to the hot water coils?
Any help will be much appreciated.
Regards
Ahmad

Ahmad Fraij's picture
Offline
Joined: 2020-10-13
Reputation: 0

Hi Ahmad,
Heat pump chillers in eQUEST can serve chilled water loops and 2-pipe loops. To serve hot water loads, you have to use a 2-pipe loop. I like to model heat pump chillers with a 2-pipe loop that is dedicated to heating loads by using a high outdoor snap temperature. Heat pump chillers are covered in the help documentation as water-to-water heat pumps. I suggest you join the equest-users list equest-users at lists.onebuilding.org.

[cid:image001.png at 01D6A071.FBF5D8F0]

Regards,
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2][Logo Description automatically generated]
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com www.pathfinder-ea.com
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image006.png at 01D6A071.FBF5D8F0] Ask me why Carbon Fee & Dividend may be right for you.

Bill Bishop's picture
Offline
Joined: 2012-02-25
Reputation: 7

Hello Bill,
Than you very much for the help.
I have changed the hot water loop to 2-pipe and selected the chiller heat pump and assigned it to the hot water loop but I received the below error. Could you please help me out in this. Further, can I select "air cooled" in the condenser tab?

Regards
Ahmad
On Monday, 12 October 2020, 11:31:05 pm AEDT, Bishop, Bill wrote:

Hi Ahmad,

Heat pump chillers in eQUEST can serve chilled water loops and 2-pipe loops. To serve hot water loads, you have to use a 2-pipe loop. I like to model heat pump chillers with a 2-pipe loop that is dedicated to heating loads by using a high outdoor snap temperature. Heat pump chillers are covered in the help documentation as water-to-water heat pumps. I suggest you join the equest-users listequest-users at lists.onebuilding.org.

?

?

Regards,

~Bill

?

William Bishop, PE, BEMP, BEAP, CEM, LEED AP

Senior Energy Engineer

T: (585) 698-1956???????????????????????F: (585) 325-6005

bbishop at pathfinder-ea.com????????www.pathfinder-ea.com

134 South Fitzhugh Street

Rochester, NY 14608?????????????????????Ask me why Carbon Fee & Dividend may be right for you.

?