Hello All,

I am doing an Appendix G model for a warehouse building that has a
semi-heated space for freeze protection only by using infrared heaters. But
it is a 35,000 SFT warehouse building and if I go by Table G3.1.1A the
system type to be used will be System 5 Packaged VAV with Reheat in the
Baseline 90.1 model and I would have infrared radiant heaters in the
proposed model. Should I use the same system type in both Baseline and
Proposed model i.e. infrared radiant heaters with same efficiencies and
temperature setpoints or can the Baseline system be Packaged VAV with
Reheat and infrared radaint heaters in the proposed model ?

Thank You

Syed Hussaini, PE, LEED GA

Energy Engineer II
------------------------------

*Partner **Energy*

680 Knox St., Suite 150 |Los Angeles, CA 90502
D: 310-622-8851 | C: 480-512-9739 | F: 310-862-2399

www.ptrenergy.com | shussaini at ptrenergy.com

P please consider the environment before printing this e-mail

Syed Safiuddin Hussaini's picture
Joined: 2016-01-22
Reputation: 0

I think your Baseline HVAC system should be System #9 or #10

[cid:cca26451-57e3-4b63-90fc-03001bcf3cf3]

[cid:d3f17c0d-1e94-4a5f-9dd5-04adecd65c2f]
James V Dirkes II, PE, BEMP, BCxP
Team Lead - Building Performance
616 450 8653
Foresight Management
https://fsmgmt.co/
LinkedIn

Coffee Conversation:

Are we mistaking an increase of communication for an increase of communion? Is basic human loneliness driving us ever deeper into a culture of dislocated virtual relationships that temporarily relieve symptoms but worsen the disease?

Jim Dirkes's picture
Offline
Joined: 2019-05-22
Reputation: 0

Jim,

Thank for sending this info. Actually ASHRAE 90.1-2007 code did not have
this option for semi heated spaces which I was using for a 179d project.
This makes sense.

Thank You

Syed Hussaini, PE, LEED GA

Energy Engineer II
------------------------------

*Partner **Energy*

680 Knox St., Suite 150 |Los Angeles, CA 90502
D: 310-622-8851 | C: 480-512-9739 | F: 310-862-2399

www.ptrenergy.com | shussaini at ptrenergy.com

P please consider the environment before printing this e-mail

Syed Safiuddin Hussaini's picture
Joined: 2016-01-22
Reputation: 0

Hi Syed,

The baseline system types are only applicable to conditioned portions of the building (hence why exception a) to Section G3.1.1 uses the term conditioned floor area). Therefore, since you indicate that the Proposed design is semiheated for freeze protection only (you should double check the definition of semiheated space in the Section 3.2 definitions though), the Baseline System would be modeled as heating only of the same type as the proposed, but you can take credit for any efficiency improvements if applicable.

Alex

Alex Chapin EIT, BEMP, LEED AP BD+C, O+M
Energy Engineer | Mason & Hanger
A Day & Zimmermann Company
O 804.521.7072
4880 Sadler Road, Suite 300 | Glen Allen, VA 23060
masonandhanger.com

An ISO 9001 Certified Company

Building a More Secure World ?

CAUTION - THIS EMAIL MAY CONTAIN CONFIDENTIAL INFORMATION

This electronic mail transmission and any accompanying documents may contain information belonging to the sender, which may be proprietary, confidential, and/or otherwise subject to restrictions on disclosure beyond the intended recipient. This information is intended only for the use of the individual or entity to whom this electronic mail transmission was sent as indicated above. If you are not the intended recipient, any disclosure, copying, distribution, or action taken in reliance on the contents of the information contained in this transmission is strictly prohibited. If you have received this transmission in error, please call 1-703-955-5702 and delete this transmission. Thank you.

ChapinAN's picture
Offline
Joined: 2019-01-19
Reputation: 0

Hi Alex,

Ok, I see. Thanks for sending this info. Yes it all points to modelling the
same heating system in baseline and proposed and efficiency improvements or
credits for infrared heaters can be taken into account.

Thank You

Syed Hussaini, PE, LEED GA

Energy Engineer II
------------------------------

*Partner **Energy*