Problem with Modeling Heat Recovery

2 posts / 0 new
Last post

Hi All,

I?m trying to model heat recovery on an AHU system, but I?m running into
problems. The AHU supply is at 8000 cfm and return fan is at 4500 cfm. My
problem is that I cannot get the heat recovery to work unless the supply
and return flows are close to each other, but if I set the return flow
close to the supply flow, my fan electrical consumption will increase. Does
anyone know a way to get around this, or the only option I have is to set
my supply and return flows to be the same? I appreciate any input from you
guys.

Thanks,

Behnam

--
Behnam Jowkar, MASc, BEng, LEED AP BD+C
Mechanical Engineer In Training
p: 416-716-5758
e: behnamjowkar at gmail.com

behnam jowkar2's picture
Offline
Joined: 2014-04-08
Reputation: 0

Behnam,

You need to reduce the effectiveness of your heat recovery system to account for less energy (air) in the exhaust stream so the heat transfer matches the design.

Unfortunately eQUEST does not allow you to separate general exhaust from local exhaust (kitchen hood, fume hood, etc.).

Hope that makes sense.

Fred