Notice: unserialize(): Error at offset 2 of 27 bytes in /var/www/includes/bootstrap.inc on line 566 Notice: unserialize(): Error at offset 2 of 28 bytes in /var/www/includes/bootstrap.inc on line 566 Notice: unserialize(): Error at offset 2 of 27 bytes in /var/www/includes/bootstrap.inc on line 566 Notice: unserialize(): Error at offset 2 of 29 bytes in /var/www/includes/bootstrap.inc on line 566 Notice: unserialize(): Error at offset 2 of 27 bytes in /var/www/includes/bootstrap.inc on line 566 Minimum Efficiency of VTAC System | Energy-Models.com

Minimum Efficiency of VTAC System

2 posts / 0 new
Last post

Hello,

We have 1 ton single package vertical heat pump in each apartment of a
multi-family building. For minimum efficiency as per ASHRAE 90.1-2007.
should these systems be compared with Table 6.8.1D *PTHP* system or *SPVHP*?

Please let me know.

Thanks,

Sunayana

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

The answer depends on your goal:

If you are looking for mandatory efficiency requirements for code
compliance, you would compare to the SPVHP numbers.

For Energy Cost Budget method or Appendix G analysis, you would use the
PTHP as your baseline system type, so you would use PTHP numbers as your
baseline efficiency.
Hope that helps! Cheers,
Elizabeth

*Elizabeth Gillmor PE, BEMP, LC, LEED AP*

*e n e r g e t i c s **consulting engineers, llc*