Mapping DOAS in Energy Cost Budget

3 posts / 0 new
Last post

Hello,

I?m working on a hotel that has an air cooled chiller, the guest rooms are
conditioned by fan coil units and the outdoor air is provided via a DOAS
that uses natural gas for heating. According to the energy cost budget
method each system should be mapped one-to-one on figure 11.5.2. The fan
coils will be mapped as system 8 (heat pump), but I am not sure how to map
the dedicated outside air system, I thought to model it identical to the
proposed building, but that means a chiller needs to be added to the
baseline model which does not make sense to me. I thought of using only
system 8 for conditioning and providing the outside air to the guest rooms,
but the energy cost budget requires to model the secondary heating source
identical to the proposed model so I am not sure how to separate the
heating source for outside air from the space heating. Any thoughts on how
to model the baseline?

Thank you,

Saif's picture
Offline
Joined: 2016-07-24
Reputation: 0

Can you please provide a more detailed description of the proposed guest room fan coils? Are they water source heat pumps? Are only the DOAS served by the chiller?

Sheila
Sent from my iPhone

Sheila Sagerer's picture
Offline
Joined: 2018-01-06
Reputation: 0

Sheila,

The guest rooms are using chilled water for cooling and electric element for heating.

David,

system 8 is packaged terminal heat pump as can see in the screenshot below