Lab Space ACH

2 posts / 0 new
Last post

I have a large 4 story building that i am modeling that is about 50 % lab
space set to 12 ACH and 100% OA and constant volume. I have created a
parametric run to turn down to 6 ACH and i am getting the same CFM and
utility bill information. Is there something i might be missing as an input
to either the model or the parametric run?

any help is greatly appreciated,

--
Rob Hudson

rdh4176's picture
Offline
Joined: 2011-02-14
Reputation: 0