Heat recovery working too well?

3 posts / 0 new
Last post

Has anyone else come across heat recovery giving very good results in their model that are higher than expected. In a heating dominated climate, we have a PSZ system serving 5 zones, with baseboards used to meet heating loads in the slave zones (they've been hard sized to just get the unmet hours in an acceptable range).

I have broken down an analysis of building heating energy by month, from LS-D and SS-D. Assuming the SS-D account for all 'building' loads (envelope, infiltration, lights, etc), and SS-D is all that, plus the OA load. For a 50% effective ERV (and no additional fan heat), I get the following for winter months:

Monthly Heating Energy Used (MBTU)

Envelope Loads (LS-D) no ERV

Envelope and OA energy (SS-D) no ERV

Envelope and OA energy (SS-D) with ERV

Envelope energy as % of total (LS-D/SS-D) no ERV

Reduction of energy in SS-D due to ERV (at 50% eff)

J

126

222

154

0.5676

0.306

F

112

196

135

0.5714

0.311

M

90

157

101

0.5732

0.357

A

54

82

47

0.6585

0.427

O

37

52

27

0.7115

0.481

N

67

112

70

0.5982

0.375

D

108

187

127

0.5775

0.321

E.g. in January a 50% eff ERV gives a 30% reduction in heating energy, even though the 'building' pre-OA accounts for 55% of the total energy. My gut feeling is that the 55% is not accurate and it is actually lower, but I can't convince myself using the reports.

Fiddling with the heat recovery control schemes doesn't seem to change the heating results by much either, however changing the effectiveness has a big impact to the results. In comparison, improving the wall performance has a relatively small impact.

I should say that this is a preliminary model so no design drawings available, and it a retail space with about 0.18 cfm OA/sqft.

Adam Barker, MBSc, C.E.T., LEED AP BD+C
Energy Project Manager
Provident Energy Management Inc.
T: 416-736-0630 x 1874 | abarker at pemi.com

AdamB's picture
Offline
Joined: 2011-12-22
Reputation: 0

HI Glenn,

I had not. After looking at this for a long time, my suspicion is that I am misinterpreting the reports somehow. So that is good know.

AdamB's picture
Offline
Joined: 2011-12-22
Reputation: 0

Hmm, I would be careful about using the LS-D reports in this way. The OA load is not precisely equal to the SS-D energy minus the LS-D energy. The miscellaneous and lighting loads also need to be considered, and it is important to remember that in zones with baseboards, the heating load will be met by the baseboards first and then the system. In addition, the LS-D reports are calculated in advance of the systems calculations assuming constant zone temperatures. Corrections to this calculation are made by the systems calculations.

If you are unsure about the results, you might want to try varying the outdoor air flow rates, the effectiveness, and the effective R-value of the envelope to see if the results you are getting make sense. You could also try limiting the calculation to a single day in January and doing some hand calculations of the envelope and OA loads to see if the results are making sense. I recommend looking at the ERV reports as well, they tend to give a fair bit of information about the energy savings from energy recovery alone.

Hope that helps,
Dan

?