Good Day eQuest-users,
I apologize if anyone can help me in the following use, there is a VAV with reheat system, DX cooling and Hot Water Reheat. The Hot Water reheat is supplied by a boiler. The building is one floor with perimeter and core zones.
The following issue cause excessive unmet load hours in heating, I figure out that changing Heat/Rehat: Hot Water delta F from 30 F to 20 F reduce unmet load hours but cooling capacity is increased tremendously, also the following warning is maintained.
Please, any of you have go ahead with the following warning?
**WARNING**********************************************************************
ZONE EL1 WSW Zone (fG.z1)
might have insufficient heating capability.
Check that the SYSTEM or ZONE HEATING-CAPACITY plus this
ZONEs BASEBOARD-RATING is adequate to maintain the ZONE
specified DESIGN-HEAT-T for the calculated peak ZONE load
(see LS-A or LS-B for the ZONE peak load.)
SYSTEM S1 Sys (PVAVS)
which supplies the above listed ZONE, has a design heating
coil exit temperature, HEAT-SET-T,(plus any zone reheat)
below its MAX-SUPPLY-T or the ZONE DESIGN-HEAT-T, which
might account for the insufficient heating capability.
ZONE EL1 WSW Zone (fG.z1) has a THERMOSTAT-TYPE
of REVERSE-ACTION, which, when added to the issues listed
in the messages above, will cause excessive underheating.
Thank you!
SUMAC
Dante Garcia, LEED AP BD+C
Tel: +511.253.5355 Anexo 16 (Lima, Per?)
Cel: +51.989.685.769 (Lima, Per?)
Hi Dante:
It always helps to include your .INP and .PD2 files on your email to this forum, so experts can help you.
Without seeing anything more, I would increase the deadband in your deadband thermostat from 2 to 4 06 6 DegF. I would also set the the COOL-CONTROL to WARMEST.
Otherwise, please attach your files. And let us know which version of eQuest you are using.
John R. Aulbach, PE
Los Angeles CA USA
Good Day eQuest-users,
I apologize if anyone can help me in the following use, there is a VAV with reheat system, DX cooling and Hot Water Reheat. The Hot Water reheat is supplied by a boiler. The building is one floor with perimeter and core zones.
The following issue cause excessive unmet load hours in heating, I figure out that changing Heat/Rehat: Hot Water delta F from 30 F to 20 F reduce unmet load hours but cooling capacity is increased tremendously, also the following warning is maintained.
Please, any of you have go ahead with the following warning?
**WARNING**********************************************************************
ZONE EL1 WSW Zone (fG.z1)
might have insufficient heating capability.
Check that the SYSTEM or ZONE HEATING-CAPACITY plus this
ZONEs BASEBOARD-RATING is adequate to maintain the ZONE
specified DESIGN-HEAT-T for the calculated peak ZONE load
(see LS-A or LS-B for the ZONE peak load.)
SYSTEM S1 Sys (PVAVS)
which supplies the above listed ZONE, has a design heating
coil exit temperature, HEAT-SET-T,(plus any zone reheat)
below its MAX-SUPPLY-T or the ZONE DESIGN-HEAT-T, which
might account for the insufficient heating capability.
ZONE EL1 WSW Zone (fG.z1) has a THERMOSTAT-TYPE
of REVERSE-ACTION, which, when added to the issues listed
in the messages above, will cause excessive underheating.
Thank you!
SUMAC
Dante Garcia, LEED AP BD+C
Tel: +511.253.5355 Anexo 16 (Lima, Per?)
Cel: +51.989.685.769 (Lima, Per?)
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
Hi John,
Here in Attached INP and PD2 files,
I have tried your recommendations before without success, eQuest version is 3-65.
Thank you!
SUMAC
Dante Garcia, LEED AP BD+C | Analista LEED Energ?a
Tel: +511.253.5355 Anexo 16 (Lima, Per?)
Cel: +51.989.685.769 (Lima, Per?)
Tel: +593.4.600.0613 (Guayaquil, Ecuador)
Tel: + 571.3151985 (Bogot?, Colombia)
Tel: +1.773.857.7906 (Chicago, USA)
dgarcia at sumacinc.com
www.sumacinc.com
De: John Aulbach [mailto:jra_sac at yahoo.com]
Enviado el: viernes, 07 de noviembre de 2014 06:31 p.m.
Para: Dante Garcia; equest-users at lists.onebuilding.org
Asunto: Re: [Equest-users] excessive underheating
Hi Dante:
It always helps to include your .INP and .PD2 files on your email to this forum, so experts can help you.
Without seeing anything more, I would increase the deadband in your deadband thermostat from 2 to 4 06 6 DegF. I would also set the the COOL-CONTROL to WARMEST.
Otherwise, please attach your files. And let us know which version of eQuest you are using.
John R. Aulbach, PE
Los Angeles CA USA
Good Day eQuest-users,
I apologize if anyone can help me in the following use, there is a VAV with reheat system, DX cooling and Hot Water Reheat. The Hot Water reheat is supplied by a boiler. The building is one floor with perimeter and core zones.
The following issue cause excessive unmet load hours in heating, I figure out that changing Heat/Rehat: Hot Water delta F from 30 F to 20 F reduce unmet load hours but cooling capacity is increased tremendously, also the following warning is maintained.
Please, any of you have go ahead with the following warning?
**WARNING**********************************************************************
ZONE EL1 WSW Zone (fG.z1)
might have insufficient heating capability.
Check that the SYSTEM or ZONE HEATING-CAPACITY plus this
ZONEs BASEBOARD-RATING is adequate to maintain the ZONE
specified DESIGN-HEAT-T for the calculated peak ZONE load
(see LS-A or LS-B for the ZONE peak load.)
SYSTEM S1 Sys (PVAVS)
which supplies the above listed ZONE, has a design heating
coil exit temperature, HEAT-SET-T,(plus any zone reheat)
below its MAX-SUPPLY-T or the ZONE DESIGN-HEAT-T, which
might account for the insufficient heating capability.
ZONE EL1 WSW Zone (fG.z1) has a THERMOSTAT-TYPE
of REVERSE-ACTION, which, when added to the issues listed
in the messages above, will cause excessive underheating.
Thank you!
SUMAC
Dante Garcia, LEED AP BD+C