Here is a system description:
----Cooling source: 1-six chillers divided to three groups, the chilled
water temp is 16C/11C and then 11C to 6C.Together with six open cooling
towers.
2-two water cooled screw heat pumps(with CH2OH.CH2OH as refrigerating
medium), with two closed cooling tower.
----Heating source: two water cooled screw heat pumps described above.There
do not have any ground souce system, so it seems that the closed cooling
tower is the heating source, although I do not quite clear about its
working theory.
My model way:
---Cooling system: due to some complex project scheduling issues, we can
not have the single chiller curve (Ref:
http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2011-April/008617.html
) So just model it as the common system, with chilled water temperature
16C/11C.
---Heating system: model as "heat pump" in equest with lake/well loop and
ground loop heat exchanger. Get flow rate from .sim output, and enter the
power(closed cooing towers plus pumps) as process load in equest.
Well, I understand this may be not the best way, but I would like to hear
from you if any of you have better ideas.
Best Regards,
Fiona You