Simulation Run Terminates when generating reports

4 posts / 0 new
Last post

I am getting my model to simulate performance. However, it's terminating when producing Summary and Verification reports with the following error shown below.

Is there a way to trace where the error is?

Thank you.

[cid:image001.png at 01CE0061.F49C1320]

MICHAEL RAIVA, P.Eng., LEED(r) AP

Mike Raiva's picture
Offline
Joined: 2013-02-14
Reputation: 0

Here is the error that I getting.

***ERROR***********************************************************************
In EL1 Sys7 (VAVS) (G.WSW16) , cooling coil leaving temperature must
be at least 6F higher than entering water temp.

MICHAEL RAIVA, P.Eng., LEED? AP

Mike Raiva's picture
Offline
Joined: 2013-02-14
Reputation: 0

I would check your coil temps, and also make sure your supply air temp is sufficiently higher than your coil temp.

Vikram Sami, LEED AP BD+C

Sami, Vikram's picture
Offline
Joined: 2011-09-30
Reputation: -1

it is based on the position of your fan. Check if it is "draw through" or
"blow through" fan and accordingly calculate your coil temp. Your supply
temperature should be 6-8 deg. higher than your coil temp.