I am getting my model to simulate performance. However, it's terminating when producing Summary and Verification reports with the following error shown below.
Is there a way to trace where the error is?
Thank you.
[cid:image001.png at 01CE0061.F49C1320]
MICHAEL RAIVA, P.Eng., LEED(r) AP
Here is the error that I getting.
***ERROR***********************************************************************
In EL1 Sys7 (VAVS) (G.WSW16) , cooling coil leaving temperature must
be at least 6F higher than entering water temp.
MICHAEL RAIVA, P.Eng., LEED? AP
I would check your coil temps, and also make sure your supply air temp is sufficiently higher than your coil temp.
Vikram Sami, LEED AP BD+C
it is based on the position of your fan. Check if it is "draw through" or
"blow through" fan and accordingly calculate your coil temp. Your supply
temperature should be 6-8 deg. higher than your coil temp.