For determining the baseline system type, 90.1-2007 Appendix G, G3.1.1 list exceptions for determining the baseline system type. Exception (b) states that spaces with a peak thermal load that differs by 10 Btu/h*ft2 or more from the average of the other spaces served by the system are to be on a separate single zone system.
My question is about the word ?served?. Are plenum and unconditioned zones on the system to be included in determining the average peak load? These spaces aren?t really ?served? by the system.
I supposed plenums could be considered as served if the return air path is through the plenum?
Or do I assume all spaces on the system are ?served? regardless of the space type (conditioned, unconditioned, plenum)?
[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056
www.wspgroup.com
________________________________
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP?s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com