Hello,
I am working on a building comprising three main zones. One of these zones
has a 100% OA requirement. I would like for eQuest to auto size the supply
cfm for all zones, thus in the wizard I do not specify any flowrate or OA%.
Once in the detailed mode, under the "Outdoor Air" tab and the "Outside Air
and Economizer" screen, I set the minimum outside air ratio to 1.0. After
running the simulation and checking the SV-A report, it says that the OA%
for this zone for the simulation was actually 3%, not the 100% this zone
requires. Can anyone tell me how to force eQuest to 100% OA? I looked at
the help for the outside air ratio and it stated that it was for winter
heating periods. Is there a work around for this? I have attached the .inp
and .pd2 files for this project.
Thank you for your assistance.
Marcus Eliason