Hi John-
Wouldn't it be nice if ASHRAE had just defined unloading curves like they
should have? Anyway, I'll take a stab at this...
It would've been nice for the reviewer to site his or her source. I think
the document being referred to is this:
http://www1.eere.energy.gov/buildings/appliance_standards/residential/pdfs/cac_tp_101105.pdf
Cutting straight to the issue:
The TRACE default 90.1-2007 heatpump shuts off at the minimum operating
temperature of 40 degrees F and switches to backup heat. There's a lot of
ways you could create custom biquadratic curves so that between 40 and 17
you have a "series" arrangement - but that won't solve the problem (because
the loading curves would need to change from project to project anyway,
given that there are no defined unloading curves!)
Here's what would work:
1) Copy the 90.1-2007 equipment in the TRACE library and reset the minimum
operating temperature to 17 degrees
2) Use this as your new heat pump
3) Run the simulation with this new equipment
4) From the equipment energy consumption report, get the total kw-hr in
heating mode for the heatpump
5) Same report - Get the total KW-hr of the auxiliary electric resistance
heating
6) Go into the visualizer and get the total KBtu-s on the heating coil for
the heatpump systems
7) Take the total Kbtu-s divided by the total kW-hrs (from 4&5) and that is
your current HSPF (It needs to equal to or higher than the HSPF in 6.8.1)
8) If the HSPF is lower than required by 6.8.1, adjust your efficiency of
your heat pump (or alternatively of your Electric resistance equipment) and
reiterate until you get an HSPF equal to or greater than that in 6.8.1.
This is textbook "Thermodynamically similar" - so that should work.
Obviously, it is best to get the HSPF to be EXACTLY the same as specified
to maximize your energy in the baseline building.
Have a great weekend
Bob Fassbender
Energy-models.com