Hi Guys!

I'm trying to model the Ventilation on the Baseline System 7(VAV with Reheat) based on Ashrae-2007.

My Proposed building uses 100% Fresh Air with Demand Control Ventilation and Heat Recovery wheels.
Most of the office spaces inside have an area greater than 500sqft.

I'm trying to understand how the Ventilation rate for baseline for such a building should be modelled.
-Would the Baseline have same Ventilation as the Proposed OR
-Would I have to use Ashrae 62.1 Ventilation (Fresh) Air rates for all zones/Rooms ?

Studying :-
The Table 1.4 and Appendix G of Ashrae 90.1 says:
-Demand control ventilation is modeled in the Baseline case for all spaces larger than 500 square feet that have a design occupancy for ventilation of greater than 40 people per 1,000 sf of floor area (except for spaces served by Baseline systems that do not have one of the following: an air-side economizer, automatic modulating control of the outdoor air damper, or a design outdoor airflow of greater than 3,000 cfm) per G3.1.2.5 / 6.4.3.9

-The minimum outdoor air ventilation rates (including infiltration) are the same for the Proposed and Baseline building designs consistent with Section G3.1.2.5 unless demand control ventilation is modeled for credit, in which case, the ASHRAE 62.1 minimum ventilation rates from IEQp1 are modeled for all Baseline systems where credit is taken for demand control ventilation.

Best Regards
Kumar

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

Hi Kumar,

I think you've answered your query already...

For LEED specifically, the baseline ventilation rates should match the
minimums documented under IEQp1 (i.e. 62.1). I would have those minimum
OA quantities delivered during all occupied (system ON) hours. The
exception in the baseline case would be for any spaces for which DCV is
already required under 6.4 provisions (assembly, conference rooms,
auditoriums, and similar areas will pass the occupancy density
threshold). If DCV is required under 6.4, model that in both baseline
and proposed cases in a consistent fashion.

One point of confusion in this matter might lie in your phrasing "my
proposed building uses 100% fresh air..." I would interpret that to
mean you have airside economizer capacity capable of delivering 100% of
design airflow rates, but that should have zero direct bearing on your
baseline case systems. Baseline system economizer function (if
occurring at all) should be determined in accordance with G3.1.2.6 & 7.

Hope that helps you keep rolling!

~Nick

Nick Caton, P.E.

Senior Energy Engineer
Energy and Sustainability Services