Outdoor Air - Minimum Air ScheduleSubject: [Equest-users] Outdoor Air - Minimum Air Schedule

3 posts / 0 new
Last post

Dear all,

I have a question about Minimum Air Schedule. The Item help said "A value of -999 returns the hourly value to MIN-OUTSIDE-AIR or to the program's calculated minimum outside air value (found on report SV-A for the SYSTEM or for each zone for zonal systems)." But the schedule can only use type "Fraction" which's value can only be 0.0000 to 1.0000. If I put -999 in this type schedule, it will be error. How to use -999 in this schedule?
[cid:image001.png at 01D223A5.FA5E3660]

Fiona Xiang LEED AP BD+C
Project Engineer
Faithful+Gould

[https://www.fgould.com/media/portal/img/signature-my-profile-btn.jpg]

Tel: +86 (21) 6080 2100 DDI: +86 (21) 6080 2424 Mob: +86 180 1853 6552

[https://www.fgould.com/media/resources/signatures/3/logo.png]

________________________________

This email and any attached files are confidential and copyright protected. If you are not the addressee, any dissemination of this communication is strictly prohibited. Unless otherwise expressly agreed in writing, nothing stated in this communication shall be legally binding.

The ultimate parent company of the Atkins Group is WS Atkins plc. Registered in England No. 1885586. Registered Office Woodcote Grove, Ashley Road, Epsom, Surrey KT18 5BW. A list of wholly owned Atkins Group companies registered in the United Kingdom and locations around the world can be found at http://www.atkinsglobal.com/site-services/group-company-registration-details

Consider the environment. Please don't print this e-mail unless you really need to.

Anonymous's picture
Anonymous

Hi Fiona!

In this instance, you can assign either a fraction schedule or a frac/design schedule (permitting values of -999).

Good to know: While the supporting documentation usually gets the job done, the reference manual help entries do not always clearly specify every option available in their descriptions. I've found generally, if you right-click a field that would require a schedule and select "View Default/Range" you'll find a more direct summary of what options are on the table:
[cid:image002.png at 01D223A9.90015FA0]
[cid:image007.png at 01D223A9.90015FA0]
[cid:image008.png at 01D223A9.90015FA0]

Best regards,

~Nick

[cid:image009.png at 01D223A9.90015FA0]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Energy and Sustainability Services
Schneider Electric

D 913.564.6361
M 785.410.3317
E nicholas.caton at schneider-electric.com
F 913.564.6380

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

[cid:image001.png at 01D189AB.58634A10]

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

Thank you Nick! You did me a big favor!!!