Heat Recovery Chiller

2 posts / 0 new
Last post

I am modeling a building that will have one chiller as a heat recovery
chiller. The design will heat reject into the domestic water loop. I am
seeing a BDL error saying HTREC-DT must be less than or equal to 70.
Without clearing this error I am not able to run a simulation. Can anyone
advise how to clear this error?

As always I am grateful to this community of experts.

Thanks

Mike Hupel, B.Tech, CEM, LEED AP

Michael Hupel's picture
Offline
Joined: 2012-01-20
Reputation: 0

Hi Michael. HTREC-DT has to be less than 70. Thats found on the Loop
Attachments tab of your chiller. It defaults to the dT of your HW loop, so
if thats over 70 you'll need to change the value of HTREC-DT.

Mike

Michael Wilson, P.Eng.

Michael Wilson's picture
Offline
Joined: 2012-01-14
Reputation: 0