[Equest-users] Multiple Heating Hot Water Loops

2 posts / 0 new
Last post

How do you model multiple temperatures for various heating HW loops such
as radiant slab (120/constant temp) vs. HW loop (160/based on OA reset)
for any type system if they are all coming from the same boiler plant?

Do you provide a heat exchanger on the peripheral loop to account for
the different temperature?

Eric Hethcoat, P.E.

Ehethcoat's picture
Offline
Joined: 2011-09-30
Reputation: 0

eQuest allows you to create secondary loops with different design temperatures. Right click on project, create a new circulation loop of type Hot Water, choose secondary subtype, select the primary loop and specify your design temperatures. It will use a 3-way valve to mix down the temperature you specify. There may be a couple steps I'm forgetting, but this is the general direction I head in.
Jeremy

___________________________________________
Jeremy McClanathan, P.E., BEMP, HFDP, LEED(r) AP BD+C

Jeremy McClanathan's picture
Joined: 2011-09-30
Reputation: 200